Controller solving issue

Discusses use of COCO, the process simulation and modelling software suite from AmsterCHEM, downloadable from http://www.cocosimulator.org

Moderator: jasper

Post Reply
rhsrxs
Posts: 26
Joined: 24 October 2012, 21:29

Controller solving issue

Post by rhsrxs »

On the attached flowsheet I am heating an air stream and then humidifying with steam. When I change the Air heater exchanger outlet temperature, the controller C1 has trouble converging. I am using this controller C1 to make sure I have mostly condensate leaving the exchanger. Any recommendations?
Attachments
10-6-15 humidifying heated air.fsd
(23.5 KiB) Downloaded 1001 times
User avatar
jasper
Posts: 1129
Joined: 24 October 2012, 15:33
Location: Spain
Contact:

Re: Controller solving issue

Post by jasper »

The problem is that you your measured variable is vapor fraction, and if you change the temperature, I suppose you are at a stream where vapor fraction is either zero or unity. In both cases, the sensitivity of vapor fraction w.r.t. the controlled variable is zero.

You can get around this by changing the measured variable to something continuous, e.g. enthalpy (0th order continuous, 1st order discontinuous at the phase boundaries). Now of course your problem is that you need to know what enthalpy matches a vapor fraction of 0.1. If pressure is constant, this is a constant value for steam. Otherwise you could get this enthalpy from a stream that is flashed at VF = 0.01 (which you would need to add to the flowsheet, measure the enthalpy and use to connect to the set point).
Post Reply

Return to “COCO (AmsterCHEM)”